briefl explain how you can use fire safety engineering to develop a performance solution and that such solutions are recognised by the BCA as a method of demonstrating compliance – few sentences only
Answer:
Background
The Developer has commissioned a Sydney access consultant to offer a Building code of Australia 2016 assessment for a proposed commercial project, which accommodate two ‘majors’, a mini food court, specialty shops and small kiosks.
Objective
The purpose of this report is to assess a set of architectural plans against nominated DTS provisions of the Building Code of Australia 2016, identification of compliances and non- compliances, discussion of solutions to any non-compliances and recommendations to the solutions.
Documentation
The documents below has been reviewed, referenced and depend on when the report was being prepared.
Architectural Drawings
The National Construction Code: Building Code of Australia 2016 Volume One – Class 2 to 9 buildings. Australian Building Codes Board, Canberra.
The National Construction Code: Building Code of Australia 2016 Volume Two – Class 1 to 10 buildings. Australian Building Codes Board, Canberra.
The National Construction Code: Building Code of Australia 2016 Guide to the Building Code of Australia 2016. Australian Building Codes Board, Canberra.
Regulatory Framework
Based to environmental planning and assessment regulation on clause 145, the commercial building proposed must comply with the BCA. Environmental planning and assessment regulation clause 143 prohibits issuance of certificate of construction if all the criteria of fire protection and structure capability of the new building will be reduced.
Performance Solution
Fire safety engineering is involved in protecting the products which is required to be installed by legislation or installed with an objective of life safety, it can also include protecting property and similarly protecting the environment, to ensure that they achieve their respective purpose, with a perspective of achieving a minimum standard of safety, increase the confidence of the customers. The products should comply with the applicable BCA standards, to ensure that safety and work health, building and laws governing customers are achieved.
The procedure for achieving the BCA standards is through testing the products under fire protection in order to show their performance, this is done through ACCC mandatory standards and respective Australia standards. The product provided to the customers should contain laboratory accreditation status, configuration and identification of the product, time taken to test the product should be confirmed and finally the validity of the result and performance of products should be stated.
classification of the building
The summary of the proposed building is classified as per the table below.
Classification based on BCA
2, 7a and 9b
Rise in storeys
1
Total height
13.0 m
Type of construction
B
Climatic zone
Zone 8
Total area/ volume
As shown below
Floor Area and Volume
The maximum size of the fire compartment is tabled below, but this maximum floor are and volume will not be applicable on class 2 compartment.
Classification of the building
Type B
9b
Maximum floor area
15000 m2
Maximum volume
195,000 m3
B.3 BCA DEEMED-TO-SATISFY COMPLIANCE ISSUES
The comments below have been made based on the specific relevant building code of Australia(BCA) provisions, that reflects to the compliance matters that is entitled to the proposed commercial building.
Clause
Descriptions
Status
Comment
Section C: Fire resistance
Part C1: Fire resistance and stability
C1.1
The required type of Construction.
Compliance achieved
Since the building is Type B then it must comply with the construction and requirement of this type of building. Based on the photo on Appendix 1it is a photo extracted from BCA table 3 under specification C1.1.
Every component of the building must have FRL that is greater than that which is provided on the table. The Building is defined as Type B Construction.
The roof allowance at its construction entitled for non-combustibility should be base on specification of C1.1 – 3.5 which explains concession of the roof, that will apply to the proposed class 2 building.
C1.2
Calculation of Rise in Storey
Stated
The building has arise of storey 1
C1.3
Building that comprises of numerous classifications
Stated
Classification entitled to the ground floor will be applied to the top storey of being an hardware
All Type B construction requirements will be implemented.
C1.4
Mixed types of Construction
C1.5
Two storey Class 2,3 or 9c buildings
C1.6
Class 4 parts of buildings
C1.7
Open spectator stands and indoor sports stadiums
C1.8
Construction of a light weight
Compliance achieved
The wall that is buildup of lightweight materials must comply to the specification of C1.8
C1.9
Provisions are not there
C1.10
Fire Hazard Properties
The properties of fire hazard on the linings, assemblies and materials in a should comply to the specification C1.10.
Relevant material will be required to be issued for assessment in order to ensure that it complies with the description above.
Part C2
C2.1
Application of Part
Stated
The clauses C2.2, C2.3 and C2.4 does not comply with the car park which is not applicable with a sprinkler system and it do comply with specification E1.5.
C2.2
Limitations of the floor area
Achieved
The ground floor in consideration to class 9b is subjected to the floor area limitations of this clause
C2.6
Vertical separation of openings in external Walls
Achieved
Based on Type B construction building any opening that is on external wall and is above another opening that is next to it but below, whereas it vertical projection do not fall further than 450 mm outside a lower opening, then it is advisable that the opening should be separated by vertical or horizontal spandrel having FRL of about 60/60/60
C2.8
Separation of Classifications
Complied
Probably the building is having numerous different classifications that is situated next to each another; therefore each element will have the required higher FRL based on the classification concern.
Further details will be needed for assessment. The construction certificate plans are expected to comply with FRL.
C2.9
Separation of classification in different Storeys
Achieved
The building which is separated based on different classification and interlinked by columns above one another, in order to minimize the risk that may occur due to fire in one classification that may result to failure of the components of the building in the other classification on a different storey.
It will be appropriate for a car park slab is to achieve 120/120/120 for it to be able to separate the class 7a and 9b. Whereas, the slab which is between each storey should provide a minimum FRL of 90/90/90.
Part C3: PROTECTION OF OPENINGS
C3.1
Application part
Stated
Concessions for definite opening types
C3.2
Protection of Opening in External Walls
Complied
Opening found on the external wall and are within 3 m and requires FRL must comply to C3.4 of BCA
C3.4
Acceptable Methods of Protection
Achieved
The compliant solution or engagement of fire engineer will be incorporated at construction stage for provision of solutions that will satisfy the requirement of CP2.
More details will be offered provided at Construction Certificate.
C3.8
Openings in Fire-isolated Exits
Achieved
The fire exit through an external opening on the same building must comply to clause C3.4
C3.9
Service Penetrations in Fire-isolated Exits
Achieved
Fire exists is not suppose to obstructed by any services but only electrical wiring which is allowed by D2.7 (e)
C3.15
Openings for Service Installations
Stated
Compliance is promptly achievable. Co-appointment with administrations experts to guarantee consistence at development testament arrange.
SECTION D : ACCESS AND EGRESS
Part D1: provision of escape
Clause
Description
Status
Comment
D1.1
Number of Exits Required
Complied
The arrangement of adequate ways out to empower safe egress if there should be an occurrence of a crisis. D1.2 gives that all structures must have no less than one exit from every storey as sets out conditions in which in excess of one exit might be required.
D1.4
Exit Travel Distances
Complied
The passageway entryway is prominent to 6m from an exit.
D1.5
Distances between alternative exits
Complied
The layout should comply with the provisions of D1.5.
D1.6
Dimensions of exits
Complied
The exit stairs and corridors together with other paths of travel should have a minimum value of 1m in width and 2m in height.
Part D2: CONSTRUCTION OF EXITS
D2.7
Installations in Exits & Paths of Travel
Achieved
In the event that introduced in a way of movement to an exit, Electrical conveyance sheets, Communication cabinets and so forth containing engines, and so on are to be encased with non-ignitable development, and entryways are to be furnished with smoke seals to the border.
D2.19
Doorways and Doors
Complied
This applies to all entryways and refers to the sorts of entryways that can’t be utilized in structures of endorsed utilizes, the utilization of intensity worked entryways and the power required to work sliding entryways.
D2.20
Swinging Doors
Complied
The condition forbids the utilization of devices, for example, stops and handles. D2.21 likewise sets out exemptions in connection to structures where unique security plans are required in connection to the utilizations completed.
D2.23
Signs on Doors
Achieved
Utilization of signs to alarm people that the activity of smoke entryways and desperate entryways and entryways releasing structure fire secluded ways out, must not be hindered and should be introduced where they can be promptly observed.
SECTION E : Service and equipment
Part E1: Firefighting equipment
E1.3
Fire hydrants
Achieved
Fire services pump room is required to be available specifically from the street or open space, or from an entryway opening from a fire confined exit. Inward Hydrants are to be situated inside each required Fire Isolated Exit (or then again the outside stairs in lieu of a fire disengaged exit).
Note: Hydrant supporter assembly must be inside sight of the fundamental passageway of structures, generally an application to FR NSW can be made keeping in mind the end goal to get an exception from this prerequisite in the conditions
E1.4
Fire hose reels
Achieved
Fire Hose Reels are to be situated inside 4m of an exit, or found nearby an inward hydrant (other than one inside a fire segregated exit). Where framework scope isn’t accomplished by the over, extra FHR might be situated in ways of movement to an exit.
Points of interest are to be accommodated evaluation, especially the area of the fire hydrant promoter get together. Hose reels are just required in the storm cellar levels and ground floor if required.
E1.6
Portable fire extinguishers
Not applicable
Nominate relevant BCA Performance Requirements
Non-compliance
BCA clause
BCA issue
Performance Requirement/s
Additional Performance Requirement/s
Protection of Opening in External Walls
C3.2
Numerous windows within the development are within 1.5 m of
the boundary.
comply with specification C3.4
CP2
Application of Part
C2.1
Does not comply with the car park which is provided with a sprinkler
comply with specification E1.5.
CP3
(Performance Requirements from Section C or D that are also relevant)
Exit Travel Distances
D1.4
The door way entrance is greater 6m from an exit
comply with specification DP.4
Assessment Methodology
Non-compliance
BCA clause
BCA issue
Performance Requirement/s
Additional Performance Requirement/s
Assessment method
Subsystem
Reason for Assessment
Method and Subsystem/
Protection of Opening in External Walls
C3.2
Numerous windows within the development are within 1.5 m of
the boundary.
comply with specification C3.4
CP2
Qualitative and Quantitative (IFEG)
SS-C
Fire spread, impact and control
Application of Part
C2.1
Does not comply with the car park which is provided with a sprinkler
comply with specification E1.5.
CP3
(Performance Requirements from Section C or D that are also relevant)
A0.2/A0.5 (NCC)
Qualitative and Quantitative (IFEG)
SS-D
fire detection and suppression.
Exit Travel Distances
D1.4
The door way entrance is greater 6m from an exit
comply with specification DP.4
Exits to open space are available from each unit without passing through or by unprotected openings of the other unit.
SS-E
Occupant evacuation and control
Conclusion
The report explains an assessment of the proposed building based on the documentation for the proposed mixed commercial building. After the study of the given drawing plan that is prepared by the architecture it can be generally classified that most of the areas in the plan are all considered dispute with the principals of the DTS provisions of the BCA 2016 anyway a couple of things will require assistance on their examination and consultation from a Fire Engineer to give goals.
Rising up out of the assessment, it is seen that the proposed project can speedily attain consistence when the relevant performance BCA are provided with any changes of design having a state that won’t result in the need to adjust the improvement consent.
References
Bennetts, I. and Pham, L., 2016. Structural robustness and fire. In Australasian Structural Engineering Conference: ASEC 2016 (p. 155). Engineers Australia.
Board, A. B. C. (2016). National Construction Code Series Volume 1, Building Code of Australia 2016, Class 2 to 9 Buildings. Canberra: Australian Building Codes Board, 163.
Board, A. B. C. (2016). National Construction Code Volume Two: Building Code of Australia Class 1 and Class 10 Buildings. Canberra: Australian Building Codes Board.
Board, A. B. C. (2016). National Construction Code: Guide to the Building Code of Australia 2016. Canberra: Australian Building Codes Board.
Grant, W., GRANT SHARON, 2008. Sprinkler system for converting non-sprinklered buildings. U.S. Patent 7,363,987.
Moinuddin, K.A., Thomas, I., Chea, S. and Bennetts, I.D., 2007. Factors affecting the reliability of sprinkler system in Australian high rise office buildings. Fire Safety Science, 7, pp.80-80.
Nguyen, K.T., Weerasinghe, P., Mendis, P., Ngo, T. and Barnett, J., 2016. Performance of modern building façades in fire: a comprehensive review. Electronic Journal of Structural Engineering, 16, p.1.
Webb, A. and Lin, X., 2015. Slip Resistance Assessment of Carpets for Compliance to National Construction Code of Australia.
Free Membership to World’s Largest Sample Bank
To View this & another 50000+ free samples. Please put
your valid email id.
Yes, alert me for offers and important updates
Submit
Download Sample Now
Earn back the money you have spent on the downloaded sample by uploading a unique assignment/study material/research material you have. After we assess the authenticity of the uploaded content, you will get 100% money back in your wallet within 7 days.
UploadUnique Document
DocumentUnder Evaluation
Get Moneyinto Your Wallet
Total 10 pages
PAY 6 USD TO DOWNLOAD
*The content must not be available online or in our existing Database to qualify as
unique.
Cite This Work
To export a reference to this article please select a referencing stye below:
APA
MLA
Harvard
OSCOLA
Vancouver
My Assignment Help. (2020). Commercial Development. Retrieved from https://myassignmenthelp.com/free-samples/arbe3306-commercial-development/architectural-plans.html.
“Commercial Development.” My Assignment Help, 2020, https://myassignmenthelp.com/free-samples/arbe3306-commercial-development/architectural-plans.html.
My Assignment Help (2020) Commercial Development [Online]. Available from: https://myassignmenthelp.com/free-samples/arbe3306-commercial-development/architectural-plans.html[Accessed 18 December 2021].
My Assignment Help. ‘Commercial Development’ (My Assignment Help, 2020)
My Assignment Help. Commercial Development [Internet]. My Assignment Help. 2020 [cited 18 December 2021]. Available from: https://myassignmenthelp.com/free-samples/arbe3306-commercial-development/architectural-plans.html.
×
.close{position: absolute;right: 5px;z-index: 999;opacity: 1;color: #ff8b00;}
×
Thank you for your interest
The respective sample has been mail to your register email id
×
CONGRATS!
$20 Credited
successfully in your wallet.
* $5 to be used on order value more than $50. Valid for
only 1
month.
Account created successfully!
We have sent login details on your registered email.
User:
Password:
Beat the cpm homework blues with best homework helper from Myassignmenthelp.com. Join with us to ace CPM homework and to succeed in your term papers. We provide a wide array of CPM Homework help and have individual teams focussing on every core connections. Get homework help with CC1, CPM homework help with CC2 and CPM homework help with CC3. Get the tips and guidance to master any kind of CPM problems. We have easy on pocket prices and multiple discounts to make the help we provide affordable and lucrative. Join us today and see for yourself a difference in your grades.
Latest Management Samples
div#loaddata .card img {max-width: 100%;
}
MPM755 Building Success In Commerce
Download :
0 | Pages :
9
Course Code: MPM755
University: Deakin University
MyAssignmentHelp.com is not sponsored or endorsed by this college or university
Country: Australia
Answers:
Introduction
The process of developing a successful business entity requires a multidimensional analysis of several factors that relate to the internal and external environment in commerce. The areas covered in this current unit are essential in transforming the business perspective regarding the key commerce factors such as ethics, technology, culture, entrepreneurship, leadership, culture, and globalization (Nzelibe, 1996; Barza, 2…
Read
More
SNM660 Evidence Based Practice
Download :
0 | Pages :
8
Course Code: SNM660
University: The University Of Sheffield
MyAssignmentHelp.com is not sponsored or endorsed by this college or university
Country: United Kingdom
Answers:
Critical reflection on the objective, design, methodology and outcome of the research undertaken Assessment-I
Smoking and tobacco addiction is one of the few among the most basic general restorative issues, particularly to developed nations such as the UK. It has been represented that among all risk segments smoking is the fourth driving purpose behind infections and other several ailments like asthma, breathing and problems in the l…
Read
More
Tags:
Australia Maidstone Management Business management with marketing University of New South Wales Masters in Business Administration
BSBHRM513 Manage Workforce Planning
Download :
0 | Pages :
20
Course Code: BSBHRM513
University: Tafe NSW
MyAssignmentHelp.com is not sponsored or endorsed by this college or university
Country: Australia
Answer:
Task 1
1.0 Data on staff turnover and demographics
That includes the staffing information of JKL industries for the fiscal year of 2014-15, it can be said that the company is having problems related to employee turnover. For the role of Senior Manager in Sydney, the organization needs 4 managers; however, one manager is exiting. It will make one empty position which might hurt the decision making process. On the other hand, In Brisba…
Read
More
MKT2031 Issues In Small Business And Entrepreneurship
Download :
0 | Pages :
5
Course Code: MKT2031
University: University Of Northampton
MyAssignmentHelp.com is not sponsored or endorsed by this college or university
Country: United Kingdom
Answer:
Entrepreneurial ventures
Entrepreneurship is the capacity and willingness to develop, manage, and put in order operations of any business venture with an intention to make profits despite the risks that may be involved in such venture. Small and large businesses have a vital role to play in the overall performance of the economy. It is, therefore, necessary to consider the difference between entrepreneurial ventures, individual, and c…
Read
More
Tags:
Turkey Istanbul Management University of Employee Masters in Business Administration
MN506 System Management
Download :
0 | Pages :
7
Course Code: MN506
University: Melbourne Institute Of Technology
MyAssignmentHelp.com is not sponsored or endorsed by this college or university
Country: Australia
Answer:
Introduction
An operating system (OS) is defined as a system software that is installed in the systems for the management of the hardware along with the other software resources. Every computer system and mobile device requires an operating system for functioning and execution of operations. There is a great use of mobile devices such as tablets and Smartphones that has increased. One of the widely used and implemented operating syste…
Read
More
Tags:
Australia Cheltenham Computer Science Litigation and Dispute Management University of New South Wales Information Technology
Next